My lad has a traditional heating setup. cold water header in loft, hot water storage tank in bedroom and a Baxi boiler downstairs.
The other day he complained the boiler had failed and I got a friend of a friend gas fitter in to replace the gas valve. Now he says the central heating comes on with the hot water, I have just been up and confirmed, there is only the hot water on. the digital controller confirms only hot water, yet the pump is running, turn off the hot water and the pump stops. How should all this be wired, I assume the pump is wired in series with the room stat, so when central heating is on, power is always to the room stat, temperature drops, stat switches power through to pump. So I have told him till wait till weekend, I will go up with screwdrivers, torch and meter. If anyone in the know can confirm my basic guess as to how the pump should be wired it would be appreciated.
__________________
Not Grumpy, opinionated. |
![]() |
![]() |
![]() |
#2 |
Member
Mega Poster
Join Date: Jul 2008
Location: here as devil's advocate
Posts: 11,541
|
![]()
control valve jammed burgerd. hot water should come on with CH but hot water should be able to go on its own. from what i remember.
|
![]() |
![]() |
![]() |
#3 |
Guest
Posts: n/a
|
![]()
Tim,I just had a similar problem with mine and it was the throw switch beside the tank which differentiates whether you want water heating or radiator heating
|
![]() |
![]() |
#4 |
Knob faced knobster
Mega Poster
Join Date: Jan 2005
Location: Haslemere
Posts: 5,419
|
![]()
3 port valve would be my first port of call (see what I did there). You may be able to get away with just changing the motor as it saves draining any of the system down and it's a little bit cheaper as well.
__________________
2001 SV650 in shimmerin green, Not broken anymore |
![]() |
![]() |
![]() |
#5 |
Guest
Posts: n/a
|
![]()
tim the pump would run with hot water on, unless it is a gravity system, if when only hot water on the htg comes on then the zone valve, the one with the lever that moves peeps were on about is buggered, you may be able to just change the motor in the zone valve depending on type, hth
|
![]() |
![]() |
#6 |
Guest
Posts: n/a
|
![]()
damm you dirty dog, see what i did there eh eh
![]() |
![]() |
![]() |
#7 |
Knob faced knobster
Mega Poster
Join Date: Jan 2005
Location: Haslemere
Posts: 5,419
|
![]()
sorry BFM you're just toooo sloooow!
![]() Tim you'll either have a 2 port valve like this... http://www.screwfix.com/prods/31480/...otorised-Valve or a 3 port like this... http://www.screwfix.com/prods/31421/...otorised-Valve you can normally get away with just swapping the motor which looks something like this... http://www.screwfix.com/prods/28670/...chronous-Motor
__________________
2001 SV650 in shimmerin green, Not broken anymore |
![]() |
![]() |
![]() |
#8 |
Member
Mega Poster
Join Date: Mar 2004
Location: Not in Yorkshire. (Thank God)
Posts: 4,116
|
![]()
Cheers guys, I will grab a motor in the morning as the lowest cost option and give it a go. I never would have thought it would be that.
__________________
Not Grumpy, opinionated. |
![]() |
![]() |
![]() |
#9 |
Guest
Posts: n/a
|
![]()
Tim,try holding the operating lever over by hand a couple of time as they can become sticky and you may,may just get away with freeing it up.[I didn't]
These are the words of a diesel eng. not a heating engineer ![]() Last edited by Dicky Ticker; 28-10-10 at 08:29 PM. |
![]() |
![]() |
#10 | |
Knob faced knobster
Mega Poster
Join Date: Jan 2005
Location: Haslemere
Posts: 5,419
|
![]() Quote:
But for the sake of less than £15 it's worht just changing the motor
__________________
2001 SV650 in shimmerin green, Not broken anymore |
|
![]() |
![]() |
![]() |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
Underfloor heating, any plumbers? | yorkie_chris | Idle Banter | 60 | 27-11-09 11:20 PM |
Design engineers? | BanditPat | Idle Banter | 8 | 24-06-09 07:41 AM |
engineers report | Nicky S | SV Talk, Tuning & Tweaking | 25 | 21-03-09 08:38 PM |
Plumbers - combi boiler question | steveg | Idle Banter | 28 | 04-11-08 09:11 AM |
Calling all engineers | gettin2dizzy | Idle Banter | 78 | 12-03-07 04:43 PM |