Quote:
Originally Posted by Uber View Post
He's installing the bypass the old fasion way. We remove alot of gate valves and ball valves now and replace them with a auto bypass that works on pressure, they should be 22mm really so the flow rate will remain the same with the valve open thus lowering the temp on pump over run quicker..

It needs this to prevent the pump from pumping hot water nowhere.. Like has been said in theory all of your rads could have TRV's on and they could all shut down, if this happens then theres nowhere for the water to go. The bypass should be set to prevent it opening on normal operating temperatures, it should only open if the pressure increases i.e because the valves have shut.

Good boiler the Vaillant thats all we fit and have only had a hand full of problems on the thousands we fit.. 2 years warrenty too i think with yours, their customer service is very good!!!

Oh and make sure he balances the system too, i.e turning down the rads that get hottest first to throw some of that heat to the other buggers rads perhaps!!!

Hope im helping in some way!!

~Rich~
Its been a nightmare week, old boiler (Concord 255, 25yrs old) was condemmed on tuesday, got some quotes, got guy to start on monday, got some goods, he got some money then just disapeared, lucly it was just a little more than the cost of the goods. I found some good guy from the Corgi website that was able to come and start on sunday, fraction of the cost of everyone else.

Even though i had 7 TRVs to install, he recomended to only install them in the bedrooms (3) as the living room and everywhere never gets hot enough to need us to turn the temp down, i will need to change the rads soon anyway along with the hot water cylinder as its not foam insulated, just blanket.

Ile try and insist to him that he should put in a 22mm bypass and put the valve, otherwise ile have to do it myself.
__________________
OTR: KTM 690 Duke R 2015 Full Akro
SIDELINE: Kwak ZX636 A1P 2002, Red, R&G's, Yoshi, Double Bubble Screen
GONE: Kwak ZX-7R P1, Full Akro, Undertray, Screen
GONE: SV650S K2 Very Bruised & Without Fairing, Motovation Frame Sliders, R&G Ally Sprocket Toe Protector, HEL 2 Line Setup, GSXR K1 600 RWU Forks, Barnett Clutch & Springs, Penske 8981 Shock, Gilles Ti Rearsets, Steel Barends, Scottoiler, AFAM Chain & Sprockets, Twin FIAMM Horns, Skidmarx Bellypan, Full Micron Zeta Steel System, Cut down undertay.

Forum Problems & Information / Site Suggestions
TSM is offline   Reply With Quote
Old 24-11-08, 06:59 PM   #12
Rich
Member
Mega Poster
 
Rich's Avatar
 
Join Date: Nov 2006
Posts: 1,089
Default Re: Any Plumbing/Heating peeps here

Quote:
Originally Posted by TSM View Post
Even though i had 7 TRVs to install, he recomended to only install them in the bedrooms (3) as the living room and everywhere never gets hot enough to need us to turn the temp down, i will need to change the rads soon anyway along with the hot water cylinder as its not foam insulated, just blanket.

Ile try and insist to him that he should put in a 22mm bypass and put the valve, otherwise ile have to do it myself.
If only i was closer i'd come and do your rads, cylinder and bypass for you, tis a nice little job..

As for the TRV's he's talking poop, they shut down on air temp not water temp so even if you think the rads not very hot it could still be hot enough in the room for the TRV to shut down. Thats where the money saving comes in too your not heating any unwanted rooms. Plus if you have them on all you rads you can turn the TRV's down low in the rooms you don't use very much and up higher for the living room ect.. This helps to balance the system too keeping the rooms you want warm warmer than the ones you don't!!
__________________
RIP Hovis - Unlucky Boyo
Rich is offline   Reply With Quote
Old 24-11-08, 07:22 PM   #13
TSM
The Sick Man
Mega Poster
 
TSM's Avatar
 
Join Date: Nov 2004
Location: Peckham.SE.LDN
Posts: 4,768
Default Re: Any Plumbing/Heating peeps here

Quote:
Originally Posted by Uber View Post
If only i was closer i'd come and do your rads, cylinder and bypass for you, tis a nice little job..

As for the TRV's he's talking poop, they shut down on air temp not water temp so even if you think the rads not very hot it could still be hot enough in the room for the TRV to shut down. Thats where the money saving comes in too your not heating any unwanted rooms. Plus if you have them on all you rads you can turn the TRV's down low in the rooms you don't use very much and up higher for the living room ect.. This helps to balance the system too keeping the rooms you want warm warmer than the ones you don't!!
Yep i thought the same, but realy our living room never gets that warm, its 5x5x3m in size and open though to 2nd living room to aprox the same size. So the rads are always on and it never gets hot hot. There is 1 TRV, where i changed it myself.

As i said, ile need to change some of the rads as they are so old, no convectors, even the return temp of the water is high enough to not be using the full power of the 18kw boiler, and thats with all rads turned on in the house and its still not that hot. So ile add the remaining TRVs then.

Lots of insulation/upgrades to be done in this house. If i had all the tools, i would be doing most of the pipework myself, except for the gas.
__________________
OTR: KTM 690 Duke R 2015 Full Akro
SIDELINE: Kwak ZX636 A1P 2002, Red, R&G's, Yoshi, Double Bubble Screen
GONE: Kwak ZX-7R P1, Full Akro, Undertray, Screen
GONE: SV650S K2 Very Bruised & Without Fairing, Motovation Frame Sliders, R&G Ally Sprocket Toe Protector, HEL 2 Line Setup, GSXR K1 600 RWU Forks, Barnett Clutch & Springs, Penske 8981 Shock, Gilles Ti Rearsets, Steel Barends, Scottoiler, AFAM Chain & Sprockets, Twin FIAMM Horns, Skidmarx Bellypan, Full Micron Zeta Steel System, Cut down undertay.

Forum Problems & Information / Site Suggestions
TSM is offline   Reply With Quote
Old 24-11-08, 07:41 PM   #14
nakedblue650
Guest
 
Posts: n/a
Default Re: Any Plumbing/Heating peeps here

Auto hydraulic bypass required for 1) benefit of boiler & system 2) to comply with Building Regs Part 'L'.

As you have 18kw of available power it should be in 22mm.

Also you shouldn't have any rads on the primary circuit or acting as by pass (commonly mis-referred to as heat dump!).

Also if you have TRVs on all rads you obviously wouldnt have a room thermostat! Another fail! You need a room stat to comply with Building Regs again! So anyone who says otherwise is talking poop!

if you PM me I can e-mail a Part 'L' regs overview if you want it.

nb650
  Reply With Quote
Old 24-11-08, 07:44 PM   #15
TSM
The Sick Man
Mega Poster
 
TSM's Avatar
 
Join Date: Nov 2004
Location: Peckham.SE.LDN
Posts: 4,768
Default Re: Any Plumbing/Heating peeps here

Quote:
Originally Posted by nakedblue650 View Post
Auto hydraulic bypass required for 1) benefit of boiler & system 2) to comply with Building Regs Part 'L'.

As you have 18kw of available power it should be in 22mm.

Also you shouldn't have any rads on the primary circuit or acting as by pass (commonly mis-referred to as heat dump!).

Also if you have TRVs on all rads you obviously wouldnt have a room thermostat! Another fail! You need a room stat to comply with Building Regs again! So anyone who says otherwise is talking poop!

if you PM me I can e-mail a Part 'L' regs overview if you want it.

nb650
Yep i read about the 18+kw needing 22mm, plus "Part L" of regs. The rads are not in the by-pass circuit, its just between the pump and return flow.
__________________
OTR: KTM 690 Duke R 2015 Full Akro
SIDELINE: Kwak ZX636 A1P 2002, Red, R&G's, Yoshi, Double Bubble Screen
GONE: Kwak ZX-7R P1, Full Akro, Undertray, Screen
GONE: SV650S K2 Very Bruised & Without Fairing, Motovation Frame Sliders, R&G Ally Sprocket Toe Protector, HEL 2 Line Setup, GSXR K1 600 RWU Forks, Barnett Clutch & Springs, Penske 8981 Shock, Gilles Ti Rearsets, Steel Barends, Scottoiler, AFAM Chain & Sprockets, Twin FIAMM Horns, Skidmarx Bellypan, Full Micron Zeta Steel System, Cut down undertay.

Forum Problems & Information / Site Suggestions
TSM is offline   Reply With Quote
Old 24-11-08, 07:51 PM   #16
nakedblue650
Guest
 
Posts: n/a
Default Re: Any Plumbing/Heating peeps here

Have a look in the back of the installation manual at the Benchmark pages - it will tell you what is required to comply with Regs. Sooooo many people do not know what is and isnt required.

nb650
  Reply With Quote
Old 24-11-08, 10:08 PM   #17
gerbrox
Guest
 
Posts: n/a
Default Re: Any Plumbing/Heating peeps here

Quote:
Originally Posted by Uber View Post
He's installing the bypass the old fasion way. We remove alot of gate valves and ball valves now and replace them with a auto bypass that works on pressure, they should be 22mm really so the flow rate will remain the same with the valve open thus lowering the temp on pump over run quicker..

It needs this to prevent the pump from pumping hot water nowhere.. Like has been said in theory all of your rads could have TRV's on and they could all shut down, if this happens then theres nowhere for the water to go. The bypass should be set to prevent it opening on normal operating temperatures, it should only open if the pressure increases i.e because the valves have shut.

Good boiler the Vaillant thats all we fit and have only had a hand full of problems on the thousands we fit.. 2 years warrenty too i think with yours, their customer service is very good!!!

Oh and make sure he balances the system too, i.e turning down the rads that get hottest first to throw some of that heat to the other buggers rads perhaps!!!

Hope im helping in some way!!

~Rich~

If the guy is worth he weight in gold he'll balance the system correctly, i.e. measuring the flow and return with an infra red gun and balancing the temperature so that all rads are 82 / 71 (regulating at the lockshields). he'll probably just vent all the rads andensure there all heating and leave. Also gethimto flush the other rads out as they sound as though there blocked full of sh1te andalso get himto fire some inhibitor in as well.
  Reply With Quote
Old 24-11-08, 10:12 PM   #18
gerbrox
Guest
 
Posts: n/a
Default Re: Any Plumbing/Heating peeps here

Quote:
Originally Posted by nakedblue650 View Post
Auto hydraulic bypass required for 1) benefit of boiler & system 2) to comply with Building Regs Part 'L'.

As you have 18kw of available power it should be in 22mm.

Also you shouldn't have any rads on the primary circuit or acting as by pass (commonly mis-referred to as heat dump!).

Also if you have TRVs on all rads you obviously wouldnt have a room thermostat! Another fail! You need a room stat to comply with Building Regs again! So anyone who says otherwise is talking poop!

if you PM me I can e-mail a Part 'L' regs overview if you want it.

nb650

Does the Part L regs not just apply to commercial and also any new builds?

Might just be me, part L just hitting up here!!
  Reply With Quote
Old 24-11-08, 10:28 PM   #19
TSM
The Sick Man
Mega Poster
 
TSM's Avatar
 
Join Date: Nov 2004
Location: Peckham.SE.LDN
Posts: 4,768
Default Re: Any Plumbing/Heating peeps here

Quote:
Originally Posted by gerbrox View Post
If the guy is worth he weight in gold he'll balance the system correctly, i.e. measuring the flow and return with an infra red gun and balancing the temperature so that all rads are 82 / 71 (regulating at the lockshields). he'll probably just vent all the rads andensure there all heating and leave. Also gethimto flush the other rads out as they sound as though there blocked full of sh1te andalso get himto fire some inhibitor in as well.
The rads were not that bad, I flushed the system about 5/6 years ago (also replaced all the wiring) and put fernox in it. There is a little bit of, hees put in some cleaner today and tommorow he will flush it again and put inhibitor in.

Only issue has been the by-pass loop that ive not been happy with, everything else he has been good.

We will get there, slowly but surely.
__________________
OTR: KTM 690 Duke R 2015 Full Akro
SIDELINE: Kwak ZX636 A1P 2002, Red, R&G's, Yoshi, Double Bubble Screen
GONE: Kwak ZX-7R P1, Full Akro, Undertray, Screen
GONE: SV650S K2 Very Bruised & Without Fairing, Motovation Frame Sliders, R&G Ally Sprocket Toe Protector, HEL 2 Line Setup, GSXR K1 600 RWU Forks, Barnett Clutch & Springs, Penske 8981 Shock, Gilles Ti Rearsets, Steel Barends, Scottoiler, AFAM Chain & Sprockets, Twin FIAMM Horns, Skidmarx Bellypan, Full Micron Zeta Steel System, Cut down undertay.

Forum Problems & Information / Site Suggestions
TSM is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Plumbing Q: Urinal Auto Syphons BoltonSte Idle Banter 1 26-03-09 09:02 AM
Plumbing supplies DarrenSV650S Idle Banter 25 26-02-09 06:11 PM
Plumbing advice (Sort of) andyb Idle Banter 2 01-06-08 04:35 PM
Creative Plumbing... Iansv Idle Banter 4 14-03-06 06:53 PM
Home Plumbing advice required - SERIOUS independentphoto Idle Banter 9 06-03-06 01:16 AM


All times are GMT. The time now is 05:04 PM.


Powered by vBulletin® - Copyright ©2000 - 2025, Jelsoft Enterprises Ltd.